EcoTec Bioline 20 problem ?

Övrig diskussion i de allmänna forumen.
Skriv svar
kurimuri
Frö
Inlägg: 1
Blev medlem: lör 17 dec, 2016 09:20

EcoTec Bioline 20 problem ?

Inlägg av kurimuri »

Hi everybody.
I have Ecotec Bioline 20 and it already works normal at 8 years. I clean ash from all system aprox. 1 time in every month and system works very well
But this winter start problems.
Right now comes every day 1-2 times "Hot Stock Pipe Error". I don't know what to do.
In Estonia we don't have anymore Ecotec dealer eather. :(
Stegatorparn
Pannrumsfanatiker!!!!
Inlägg: 5009
Blev medlem: sön 22 jan, 2012 11:20
Ort: Kungsbacka

Re: EcoTec Bioline 20 problem ?

Inlägg av Stegatorparn »

Never heard about that alarm before. Maybe it´s like "back heat".
Do you have to reset the termal contact pos. 18 at page 4 in the manual? http://www.wv.fi/folder/Bioline_20manual713.pdf

Check if the gate wings are worn.
Check also if the short pipe between the input feeder pipe and the air distribution box is clogged.
You can see this pipe on the first picture at page 4.
Clean the pipe with a wire. You have to dismount the fan to do this.
Optiburn -22, Värmebaronen Combimax 2000 UB -94, Ulma doserskruv, ack Thermia SA500B, Thermomatic CBJ, 3 ton bulkförråd
Värmer 240m²(2pl) + 90 m² källare
xdigger
Pannrumsnisse!
Inlägg: 856
Blev medlem: tor 16 dec, 2010 21:51
Ort: Eskilstuna

Re: EcoTec Bioline 20 problem ?

Inlägg av xdigger »

When you allready have the fan away, take a toothbrush and clean the wings of the fan.
Stenhus från -58, Thermia Biomatic -03, Ecotec Bioline 20 -05, Thermomatic EC Home, EVR-C. Egensotare.